On Tue, 20 Jan 2004 14:43:38 +0000, Darren Grant
<(E-Mail Removed)> wrote:
>Traditionally yes they did, but that is no longer the case. Pressac are
>the manufacturer of the current NTE 5 and it has a Zener diode in to
>regulate incomming line voltage. At least that is what is inside the one
>they sent me.
I'm not sure you understand the purpose of a primary protective
device such as that in the NTE5. They are not designed to protect
equipment but to protect the cabling within the house by limiting
voltages and currents to levels below which the wiring might ignite.
Look at the different characteristics of the components and you will
realise either what you are looking at is either not a Zener or not
an NTE5. It cannot be a single Zener Diode connected across A&B.
A typical gas discharge device used in an NTE 5 will trigger at
between 150/250V and is capable of a surge discharge current of 5 to
ten thousand Amps for 20microseconds. It fails safe to a permanent
short circuit.
A typical Zener diode (of size capable of fitting into an NTE5
circuit board) will have a transient capability at 150V limiting of
about 13Amps for 10 microseconds. This is woefully inadequate. It
will often fail unsafe (open circuit). Zener diodes are designed for
voltage regulation, not for protection against surge impulses.
Moreover a single Zener diode is a normal diode below the Zener
voltage - it always conducts in one direction which would now make
the NTE5 line polarity dependent.
Transient Voltage Suppressors (TVS) are bipolar avalanche
semiconductor devices similar in packaging to a Zener diode which are
designed to provide secondary protection against voltage and current
transients. The silicon TVS is designed to operate in the avalanche
mode and uses a relatively large junction area to absorb large
transient currents. Even so its capacity is nothing like that of a
spark gap and it would mainly be used in equipment to remove the
spikes a spark gap will pass (and cause) before triggering. TVS's
are usually designed to fail short circuited (safe).
>> You are describing a Transorb (Metal Oxide Varistor), not a Zener
>> Diode. A Zener Diode has a defined reverse breakdown voltage above
>> which it switches very rapidly from non-conducting to conducting. A
>> Zener diode does not absorb power to any significant extent - it
>> would depend upon an associated load resistor for this.
>Yes you are correct, allthough there is a knee voltage respose on the
>reverse breakdown.
I'm not at all sure what you are taking about here.
>The Zener in the NTE 5 is classic Zener Regulator.
There is no need for a regulator on POTS circuits.
>With my limted electronics knowledge (I am not an electronics engineer)
>the resistance is found in the wire from the exchange.
The protective device is there to prevent damage from transients on
the line which can occur at any point - you cannot rely upon wiring
resistance to the exchange.
>As I understand it the line provides a 70v supply and the job of the
>Zener is to prevent it exceeding 100v.
The job of the exchange is to limit the line voltage. The job of the
primary protection device is to limit transients induced between the
exchange and the subscriber to a point where they will not pose a
danger to the wiring. The job of a secondary protective device is to
protect the equipment.
>> The only way of protecting against this is to have a filter which is
>> earthed separately from the phone lines. Effective common mode
>> filters are both expensive and big.
>
>Exactly what I said, this can not be considered protection from a
>lightning strike only over voltage from the BT Exchange.
You don't get overvoltages from BT exchanges.
>> No ADSL filter will have any measurable protective effect.
>>
>I am talking about filters in general, mainly failed Excelsus ones from
>customers who have needed to replace them.
That is an ADSL filter is it not?
>It would seem that the
>breakdown of the components in the filter has resulted in less impact on
>the connected equipment. Not by design but just one of those things that
>the components in the filter seem to take the hit.
The fact that a filter has failed does not mean it protected anything
other than the users imagination. As the circuit configuration
provides no protection it is difficult to see how you could justify
this hypothesis.
>That again is exactly what I was saying, lightning protection to most
>means consumer products such as the belkin ones. They can offer some
>protection but not a direct hit, hence the insurance.
Direct hits are not the problem (in that no consumer device will do
anything other than to melt). It is ground strikes some distance
away which produce a damaging voltage gradient.
http://www.st.com/stonline/books/pdf/docs/3690.pdf covers the
subject.
If you want to see UK lightning activity it can be viewed at
http://irishwan.org/modules.php?name...showpage&pid=8 or
http://www.meteorologica.co.uk/freedata_lightning.asp
--
Peter Parry.
http://www.wpp.ltd.uk/