2K or 4K volt isolation in network interface card (NIC) is internal
protection that can be overwhelmed IF protection is not installed where
wire enters a building. Telephone switching stations connected to
overhead wires everywhere in town work uninterrupted and undamaged
during every thunderstorm. Operating without damage is normal and
necessary when protection is properly installed.
Protection is not the protector. Yes Polyphaser protectors are
legendary. But that is not because Polyphaser protectors do something
mythical. Protectors don't stop or block damage as a 2K or 4K NIC
interface must if missing is ... well what does Polyphaser discuss
extensively? Earthing is the protection. Polyphaser protector is
superb because (when) it makes a short connection to a same earth
ground used by AC electric, phone line, cable TV, and ham radio
equipment.
If transients are properly earthed at a building entrance, then that
2K or 4K volt protection in network devices is not overwhelmed. But
again, does PoE ethernet have that common mode transient protection? I
have not seen the numbers.
PoE means protector must remain well above that voltage (42 volts?)
BellCore specs in that Polyphaser protector (because phone lines were
generations ago direct lightning strike protected) define a low voltage
protector. Galvanic isolation inside that PoE ethernet device should
be sufficient to make any transient below those BellCore specs to not
be destructive. However I don't know if a PoE spec for voltage
transient means a lower voltage earthed protector may be necessary.
Contact Polyphaser for their interpretation. Get specs (numbers) from
those PoE devices to learn of their internal protection numbers.
Whereas conventional ethernet has that 2K or 4K volt galvanic
isolation, I don't know if that also applies to power wires in PoE.
BTW, why long before WWII did we suffer direct lightning strikes
without damage - and not use fiber optics? Direct lightning strikes
without damage is routine if the human does his job in advance. I just
don't know what internal protection numbers are for the PoE wires;
whether those BellCore numbers are sufficient..
William P.N. Smith wrote:
> (E-Mail Removed) (Al Dykes) wrote:
>> CAT5 Ethernet devices are isolated at each end good for a few thousand
>> volts (4kV ?). ISTM that if you get a lightning hit close enough to
>> exceed that you're screwed in lots more ways than your APs.
>
> Well, http://geekho.com/IMG_0140.JPG probably could have been
> prevented (poor picture, but it blew the cover open) with some
> appropriate lighting arresters. The (protected) antenna on the top of
> the tower had been removed for replacement when this happened...
>
> I'm looking at http://www.polyphaser.com/datasheets/NX4-60.pdf for
> now, but they are pretty pricey, anyone have any other thoughts?
>
> Thanks!